  Modbus - Wikipedia, the free encyclopedia
Modbus allows for communication between many devices connected to the same network, for example a system that measures temperature and humidity and communicates the results to a computer.
Modbus RTU is a compact, binary representation of the data.
Modbus is restricted to addressing 254 devices on one data link, which limits the number of field devices that may be connected to a master station.
en.wikipedia.org /wiki/Modbus   (640 words)

  
 Modbus   (Site not responding. Last check: 2007-11-04)
Modbus Protocol is a messaging structure developed by Modicon in 1979, used to establish master-slave/client-server communication between intelligent devices.
Modbus is a de facto standard, truly open and the most widely used network protocol in the industrial manufacturing environment.
Modbus is an application layer messaging protocol, positioned at level 7 of the OSI model that provides client/server communication between devices connected on different types of buses or networks.
www.intellicom.se /modbus.shtml   (447 words)

  
 Modbus protocol, specifications and in depth tutorial
Modbus has its roots in the late seventies of the previous century.
The original Modbus interface ran on RS-232, but most later Modbus implementations used RS-485 because it allowed longer distances, higher speeds and the possibility of a true multi-drop network.
Modbus messages on serial connections are not sent in a plain format.
www.lammertbies.nl /comm/info/modbus.html   (1822 words)

  
 Modbus I/O, Remote Monitoring: Control Solutions
Modbus is an industrial protocol standard that has been in use for many years.
Modbus ASCII and Modbus RTU are relatively simple serial protocols that use EIA-232 or EIA-485 to transmit data packets.
Modbus protocol is defined as a master/slave protocol, meaning a device operating as a master will poll one or more devices operating as a slave.
www.csimn.com /CSI_pages/ReModbus.html   (1357 words)

  
 Regarding Modbus   (Site not responding. Last check: 2007-11-04)
Modbus ASCII format is convenient to use over a Modem because there is no guarantee that the entire Modbus packet will be send as a single Modem packet.
Modbus ASCII format is also handy to use under Windows NT where it is near impossible to get the hardware when you need it.
I'm implementing Modbus in the jModbus project (http://jmodbus.sourceforge.net) and under the java comm API this is quite difficult.
www.control.com /1004462967/index_html   (1300 words)

  
 Modbus FAQ | PLCdev
MODBUS is a common means of gathering data from many different sources for viewing operations, archiving and troubleshooting from a central remote location.
Modbus protocol establishes the format for the master's query by placing into it the device (or broadcast) address, a function code defining the requested action, any data to be sent, and an error-checking field.
The only cable required to test MODBUS is a three conductor, wired to one end with a standard 9 pin connector for the computer com port and the other end loose to tie into the customer interface terminalsThe 9 pin terminal 2 is Rx, terminal 3 is Tx, and 5 is GND (or Common).
www.plcdev.com /modbus_faq   (1777 words)

  
 Modbus TCP - Ethernet TCP/IP Client/Server Communication   (Site not responding. Last check: 2007-11-04)
Modbus is an application-layer messaging protocol, positioned at level 7 of the OSI model.
Modbus devices are certified by the Modbus-IDA User Organization for interoperability and conformance to the Modbus specification.
The well-proven Modbus services and the object model which has been available since the original Modbus protocol version are unchanged, and have simply been adapted to TCP/IP as the data transmission protocol.
www.anybus.com /eng/technologies/modbustcp.shtml   (482 words)

  
 ProtoCessor - RTU Protocol Overview
Modbus RTU is an open, serial (RS-232 or RS-485) protocol based on master/slave or client/server architecture.
The simplicity of Modbus RTU messages is a mixed blessing; on the one hand, the simple message structure ensures widespread, rapid and accurate implementation, but on the other hand, various companies have corrupted the basic 16-bit Modbus RTU register structure to pack in floating point, queues, ASCII text, tables and other types of non-Modbus data.
Modbus RTU can also be multi-dropped, or in other words, multiple slave devices can exist on one Modbus RTU network, assuming that the physical layer allows this, usually via the use of RS-485, modems or radio.
www.protocessor.com /techsupport/Modbus_RTU_Protocol_Overview.asp   (917 words)

  
 TopWorx: Modbus Overview   (Site not responding. Last check: 2007-11-04)
Modbus devices communicate over a serial network in a master/slave (request/response) type relationship using one of two transmission modes: ASCII (American Standard Code for Information Interchange) mode or RTU (Remote Terminal Unit) mode.
Modbus Plus communicates via a single twisted pair of wires and uses a token passing sequence for peer communication sequences.
Modbus is well accepted and well understood by many in the world of industrial communications.
www.topworx.com /fn_mb.html   (436 words)

  
 FieldServer - Modbus Protocol
Modbus is an application layer messaging protocol that provides client/server communication between devices connected on different types of buses and networks.
Modbus continues to enable millions of devices worldwide to communicate and it continues to grow in most industries.
Modbus ASCII – each eight-bit byte in a message is sent as two ASCII characters, main advantage is that it allows time intervals of up to one second to occur between characters without causing an error.
www.fieldserver.com /about/modbusprotocol.asp   (460 words)

  
 Eurotherm | Knowledge | Modbus   (Site not responding. Last check: 2007-11-04)
MODBUS defines a digital communication network to have only one MASTER and one or more SLAVE devices.
MODBUS TCP allows a host computer to connect to a remote serial port and to talk to a MODBUS communicating device via an interconnecting ethernet LAN using a special MODBUS TCP driver.
As far as the slave instrument is concerned, the transaction is a standard MODBUS transaction.
www.eurotherm.co.uk /uk/eng/Knowledge/Communications/Modbus.htm   (288 words)

  
 Modbus vs CAN bus   (Site not responding. Last check: 2007-11-04)
MODBUS is a software protocol whereas RS-485 is a hardware protocol (in a layman language).
Modbus RS485 means modbus protocol using RS485 as its physical connection (multi drop/slave).
Modbus is a data communications protocol that standardizes register addressing and request and response framing.
www.control.com /1026211503/index_html   (619 words)

  
 Linux based firewall for Modbus/TCP
MODBUS is one of the most widely used messaging standards for communication among industrial devices, including SCADA systems.
Modbus/TCP is a third MODBUS protocol which brings MODBUS to IP networks, Modbus/TCP is commonly used by Java applets or ActiveX controls, whereby a user can connected to the embedded web server on an industrial device download the web-based interface for monitoring the end-device and its IO points.
The Modbus module follows the same path, but examines the packets past the TCP header, because Modbus is over TCP.
modbusfw.sourceforge.net   (2039 words)

  
 Getting Started with Modbus Communication in Lookout- Developer Zone - National Instruments   (Site not responding. Last check: 2007-11-04)
Modbus TCP/IP allows for devices to be configured and accessed on an Ethernet network while still using the characteristics of the Modbus protocol.
The Modbus object is suitable for communicating with all Modbus compatible devices.
Each of these objects is based on the Modbus protocol but may be used in different situations, depending on the device with which you are communicating.
zone.ni.com /devzone/cda/tut/p/id/3381   (3590 words)

  
 Modbus RTU FieldServer Driver
Modbus defines a message structure that controllers will recognize and use, regardless of the type of networks over which they communicate.
Modbus describes the process a controller uses to request access to another device, how it will respond to requests from the other devices, and how errors will be detected and reported.
During communications on a Modbus network, the protocol determines how each controller will know its device address, recognize a message addressed to it, determine the kind of action to be taken, and extract any data or other information contained in the message.
www.fieldserver.com /products/drivers/Modbus_RTU_driver.asp   (267 words)

  
 Beckhoff Fieldbus Box for Modbus
Modbus is an open, serial communications protocol based on the master/slave architecture.
Because of the low transmission rate, which has a maximum of 38.4 kbaud, Modbus is best employed in circumstances where the number of devices participating on the bus is small and where low demands are placed on response time.
Modbus is used on a variety of transmission media.
www.beckhoff.com /english/fieldbusbox/b730.htm   (534 words)

  
 Using Touch Screens with Vision Builder AI through Modbus- Developer Zone - National Instruments   (Site not responding. Last check: 2007-11-04)
Modbus is an application layer messaging protocol for client/server communication between devices connected on a bus or network.
Modbus can be implemented using asynchronous serial transmission to communicate with touch screens, PLCs, and gateways to complement other types of industrial buses.
Per Modbus convention, the register address of the slave device, which is the PC or CVS-145x system in this case, is calculated by subtracting 1 from the register name that you specify in the master device configuration software.
zone.ni.com /devzone/cda/tut/p/id/4724   (2399 words)

  
 Modbus to Ethernet   (Site not responding. Last check: 2007-11-04)
Modbus in conjunction with Ethernet is a perfect way to achieve cost efficient, flexible, future proof and location independent solutions for Building and Industrial Automation solutions.
Modbus RTU/ASCII has been an open system since many years and today it is used in many different applications within automation.
To connect the Modbus network to Ethernet, it is possible to use the NetBiter as development platform.
www.intellicom.se /modbus_ethernet.shtml   (262 words)

  
 IA Coffee House - Modbus Protocol   (Site not responding. Last check: 2007-11-04)
Technically, Modbus is one of the early protocols used for Programmable Logic Controllers.
This allows anything from a simple door switch to a complex mega-watt steam turbine to be described as a Modbus memory.
I have been told in the days of MAP/TOP (late 1980's) Modbus II was an special serial protocol developed to communicate between a host and the MAP Token Bus NIC (perhaps by HDLC?).
www.linse.org /kopihaus/modbus.html   (1299 words)

  
 Free Windows Modbus Master
There is also a class that is used for communicate with slaves through TCP/IP network using Open Modbus protocol.
Modbus Automation Client - This is a simple application that use the ActiveX server and is intended to test the installation, read and write registers or coils.
www.pmcrae.freeserve.co.uk - Free modbus dll for windows and a simple C source code to use linux to communicate with modbus slaves.
members.tripod.com /~mbserver   (676 words)

  
 SIXNET Modbus over Ethernet, Serial RS232 / RS485 supports: Modbus TCP, Modbus UDP, Modbus RTU, and Modbus ASCII   (Site not responding. Last check: 2007-11-04)
Modbus RTU or any protocol based on gap timing is not recommended because modems may compress or change the gaps and thus interfere with the timing.
Typically it is used to transfer Modbus registers from Ethernet to a serial device.
The Modbus master must be on the Ethernet side and Modbus slave(s) on the serial side.
www.sixnetio.com /html_files/products_and_groups/modbus.htm   (445 words)

  
 Free Modbus RTU Source Code
Modbus is by far the most popular industrial automation protocol in use today.
In such cases, we would rather that they implement our tested and supported Modbus RTU source code which we are familiar with, than some other third party's code.
As defined, this Modbus RTU standard provides data in four Modbus memory map groups or data types.
www.protocessor.com /techsupport/Free_Modbus_RTU_Source_Code.asp   (610 words)

  
 Powerware Modbus Card UPS Connectivity Device FAQs
Modbus is a protocol (or language) spoken by industrially oriented equipment.
Jbus is a slight variation of the Modbus standard.
The Modbus card connects to the network via RS-485 through either an isolated DB-9 port or terminal block.
www.powerware.com /ups/connectivity/modbus_faqs.asp?CC=1   (408 words)

  
 MAT Modbus IO manual   (Site not responding. Last check: 2007-11-04)
The modbus slave module is partially implemented and has not undergone serious testing.
Access control of MatPLC points through Modbus slave is based on the standard MatPLC architectural concept: in order to write to a point the Modbus slave must be the owner of this point.
The modbus slave module, whose default name is "modbus_s", should be enabled in the MatPLC configuration with a "module" keyword and the path to the module's executable.
mat.sourceforge.net /manual/io/modbus.html   (1102 words)

  
 Modbus, Modbus Software, Modbus RTU, Modbus ASCII   (Site not responding. Last check: 2007-11-04)
Modbus Poll is the very popular master simulator for test and debug of your slave devices.
Modbus Slave is a slave simulator for simulating 32 slave devices/address areas.
This is a community for Modbus users by Modbus users.
www.modbustools.com   (107 words)

  
 [No title]
Note that masters may send out commands ‘speculatively’, and use the success or exception codes received to determine which MODBUS commands the device is willing to respond to and to determine the size of the various data regions available on the slave.
This indicates a fault in the structure of the remainder of a complex request, such as that the implied length is incorrect.
Although these functions are defined in terms of their operation on 16-bit registers, they can be used to move any type of information from one machine to another, so long as that information can be represented as a contiguous block of 16-bit words.
www.eecs.umich.edu /~modbus/documents/Open_ModbusTCP_Standard.doc   (2729 words)

  
 MODBUS Communication Libraries - Sunlux Technologies Ltd.
MODBUS is an open-standard industrial protocol used for communication with MODBUS supporting devices like Programmable Logic Controllers, Remote Terminal Units's etc. This protocol is supported by numerous devices in the industry today.
The MODBUS protocol stack is a complete, ready to use solution for adding MODBUS functionality to your Embedded Device be it a Remote Terminal Unit, a PLC or your own custom embedded device.
Evaluation Version of the MODBUS Master and Slave Source Code Libraries and other components: Sunlux provides Evaluation Versions of both the MODBUS Master and Slave Source Code Libraries as well as their Windows components in order to enable customers to try and evaluate the suitability of these libraries to their application.
www.sunlux-india.com /MODBUSProtocolSuite.htm   (663 words)

  
 Modbus-IDA Technical Resources
ModLink is a set of native VCL components that allows you to integrate the ability of communication via Modbus protocol over a variety of networks into your applications created using Borland Delphi.
A shareware program, "Modbus Poll" for Windows 95/98/ME/2000/XP, is designed primarily to help developers of Modbus slave devices or others that want to test an instrumentation device.
NModbus is a C# 2.0 implementation of the Modbus protocol.
www.modbus.org /tech.php   (784 words)